• JJROKCZ@lemmy.world
    link
    fedilink
    arrow-up
    2
    arrow-down
    6
    ·
    1 year ago

    Eh so long as they don’t ground out then they’re fine, even if they make a ground connection then the breaker will trip long before enough juice hits that pool to seriously hurt them

    • NumbersCanBeFun@kbin.social
      link
      fedilink
      arrow-up
      17
      ·
      edit-2
      1 year ago

      Yeah no thanks. I work in an electrical based industry and I can tell you for a fact that you don’t want 240v at 100 to 200 amps for even a second.

      I yelled at a tech the other day for not wearing hot gloves when working on a set of taps in a MSP. It’s not a joke and you’re gambling with your life.

      I mean think about it. Why make GFCI outlets as a redundant safety feature if the breaker was so good at catching it? The point is that you shouldn’t trust a mechanical switch to be the only thing between you and going home to your family.

      • mommykink@lemmy.world
        link
        fedilink
        arrow-up
        3
        arrow-down
        1
        ·
        1 year ago

        Where in the hell are you at that 200 amperage wall outlets are the norm?? In 99% of US homes outlets are 110v 15a which is enough to put you on your ass but certainly won’t kill you without prolong exposure or preexisting health factors

      • areyouevenreal@lemmy.antemeridiem.xyz
        link
        fedilink
        arrow-up
        1
        ·
        edit-2
        1 year ago

        A human body wouldn’t conduct that much current with mains voltage. It’s just too high resistance.

        Also pretty sure they mean breakers with GFCI as is required in some countries. If they just mean regular circuit breakers then yeah they are fucked.

        Although tbf since it has both neutral and live in the strip it would probably short and not even reach the people. As in almost no current would go through them because ground is right next to it. This would in turn cause the breaker to trip without even a GFCI getting involved potentially.

        • gingersneak@lemmy.world
          link
          fedilink
          arrow-up
          1
          ·
          1 year ago

          Lmao it will definitely conduct enough to stop your heart if you’re well grounded. In this case these morons are likely ok because they’re in an aboveground rubber pool. If they were in an in ground pool with a nice metal drain or copper pipes for the water supply, they would be conducting just dandy if they stood in the wrong place.

          • areyouevenreal@lemmy.antemeridiem.xyz
            link
            fedilink
            arrow-up
            1
            ·
            1 year ago

            Yeah you were talking about 100s of Amps. A human body won’t conduct that without a lot of voltage/potential difference. You don’t even need 1 amp to kill you though.

            Yeah if there is exposed and grounded pipe work present that changes things somewhat. The lowest resistance path is probably still back through the same power strip the electric came from through, as water isn’t the best conductor out there.

    • Justin@lemmy.jlh.name
      link
      fedilink
      arrow-up
      10
      arrow-down
      1
      ·
      1 year ago

      Only if they’re using a gfci breaker. Standard breakers trip at 7A+ which is plenty enough to kill you. In the US, this breaker is on the wall outlet, in the EU, this breaker is on the central panel.

      • areyouevenreal@lemmy.antemeridiem.xyz
        link
        fedilink
        arrow-up
        1
        ·
        1 year ago

        Bare in mind the nearest ground is also in the power strip. It probably wouldn’t go anywhere near the people. Since you also now have a short circuit it would probably trip the breaker depending on the conductivity of the water.